Question about Checking my water on my Central Boiler with the test kit

Started by adamant, December 18, 2015, 05:58:08 AM

Previous topic - Next topic

0 Members and 1 Guest are viewing this topic.

adamant

central boiler 6048
son's off to collage and he was replaced with a timber wolf tw 5

Roger2561

Quote from: adamant on December 18, 2015, 05:58:08 AM
My results is 16 drops.. am I still ok?

adamant - I don't have my manual in front of me, but I believe the desired level is between 20 and 30 drops.  Roger 
Roger

Logging logginglogging


doctorb

My advice is to go gently when you add it.  You can always add more.  Draining a portion of the system and refilling is much more time-consuming.  It may not take much to bump your drop total to 20-30 drops from 16.  I would add between a cup and a pint, no more.