Started by GeneWengert-WoodDoc, January 22, 2015, 09:08:31 AM

Previous topic - Next topic

0 Members and 1 Guest are viewing this topic.

GeneWengert-WoodDoc

When dry air (under 100% RH) is blown across of piece of undried lumber, water will be evaporated from the wood. This increases the air's RH.  A dehumidifier removes water vapor from the air, making the air drier and increasing the ability to remove more water from the lumber.

In round numbers, it takes 1000 BTUs of energy to evaporate one pound of water from wood.  That is the same as 0.293 kWH.

With 1000 board feet of oak lumber, a green load will have around 2500 pounds of water to evaporate to achieve 7% MC.  If we used electric strip heat, (or light bulbs in a simple kiln), this would mean we would need about 732 kWh of electricity just for evaporation.  Building heat losses and vent losses would double this number to 1464 kW.  At 10 cents per kWh, that is $146 total or $2.40 per 1% MC removed per 1000 BF.

A dehumidifier is a heat pump, and so it is very efficient.  A 60 pint per day unit will condense 60 pounds of water per day and use about 630 watts per hour.   This is true for any kiln  even a solar kiln with DH assist, or even in a basement.  (Any 60 pint DH that runs  continually for one hour will draw about 6 amps of current or 0.630 kWh or $.63 worth of electricity at 10 cents per kWh, which is a low rate for many people.)  So, to evaporate 2500 pounds of water will require  roughly 630 kWh or $63.  Stated another way, with 1 MBF of lumber, each 1% moisture removed  by a DH unit takes 10 kW.  That is $1 per 1% moisture removed from 1000 BF of oak.

Another comparison is that with a fairly efficient wood heating system, it will take about  1/5 of a cord of air dried oak fireood to dry 1000 BF of oak lumber in a kiln.  Perhaps that is $20 worth of wood or $0.33 per 1% per MBF.

Using natural gas in a furnace would require about $24 of gas at today's low prices, or $0.40 per 1% per MBF.

Of course air drying is free energy.  So is a 100% solar heated kiln.

Gene - Author of articles in Sawmill & Woodlot and books: Drying Hardwood Lumber; VA Tech Solar Kiln; Sawing Edging & Trimming Hardwood Lumber. And more

scsmith42

Gene, thank you for the writeup.  It's been my experience that - depending upon the time of year - in the second half of the drying cycle the heat strips are frequently operating in order to keep the kiln temp at 120F (or higher for the sterilization cycle).  Heat strip usage is higher in the winter when the ambient temps are lower too.

Have you looked at the KW consumption for the sterilization cycle, as well as the 120F cycles?
Peterson 10" WPF with 65' of track
Smith - Gallagher dedicated slabber
Tom's 3638D Baker band mill
and a mix of log handling heavy equipment.

GeneWengert-WoodDoc

Gene - Author of articles in Sawmill & Woodlot and books: Drying Hardwood Lumber; VA Tech Solar Kiln; Sawing Edging & Trimming Hardwood Lumber. And more

GeneWengert-WoodDoc

Your experience reinforces the idea that a DH kiln building should be extremely well insulated, unless the auxiliary heat comes from wood.  Oftentimes the power company or university extension can do an audit of your kiln to determine building losses and suggest energy saving ideas.
Gene - Author of articles in Sawmill & Woodlot and books: Drying Hardwood Lumber; VA Tech Solar Kiln; Sawing Edging & Trimming Hardwood Lumber. And more

FarmingSawyer

Thomas 8020, Stihl 039, Stihl 036, Homelite Super EZ, Case 385, Team of Drafts

rjwoelk

What would be the best insulation,  I was thinking spray foam, closed cell type.
Lt15 palax wood processor,3020 JD 7120 CIH 36x72 hay shed for workshop coop tractor with a duetz for power plant

GeneWengert-WoodDoc

Closed cell, due to the high moisture environment is essential.  A good poly sheet on the inside as a vapor barrier is also encouraged, patching any holes for the vents, etc.  Closed cell rigid boards will work as well as spray foam.  Some foams will not withstand temperatures much over 130 F, so these low temperature foams need to be avoided
Gene - Author of articles in Sawmill & Woodlot and books: Drying Hardwood Lumber; VA Tech Solar Kiln; Sawing Edging & Trimming Hardwood Lumber. And more

johnnyllama

Gene,
Would rigid polyisocyanurate foam with foil facing be an acceptable insulation for the kiln if it is going to be heated hot enough for sterilization? And if dehumidifiers are used will electric strip heating provide enough heat to reach sterilization temps ( with high enough r-values and sealed for air infiltration)? I'm building a 15' x 6' x 8' kiln for our own use, not commercial use, and trying to keep cost down. Considered solar but decided to go dehumidification. It's located near our outdoor boiler too so possability of running a loop from that. We would air dry most woods other than maple first.
Turner Bandmill, NH35 tractor, Stihl & Husky misc. saws, Mini-excavator, 24" planer, 8" jointer, tilting shaper, lathe, sliding table saw, widebelt sander, Beautiful hardworking wife, 2 dogs, 2 cats, 23 llamas in training to pull logs!!!

Ugly Tree

Gene,  I have access to a good mess of structurally insulated panels. Metal both sides.  I wonder if the glues used in SIPS would hold up to the high temps of solar kilns we can get them up to here in the South.  Any experience with SIPS for kilns?
Woodland HM126, Massey Ferguson 3165, 440 and 210 Stihl, a lot of grunt bars.

GeneWengert-WoodDoc

Johnnyllama:  The isocyanate has a variety of formulations, so I cannot comment about the specific product you will be using.  The manufacturer would be the best source.  A panel with foil is a good idea.  However, the key to insulation for any kiln is to have thermal stability, closed cell construction, plus adequate thickness.  As far as thickness, I would suggest 6" minimum for walls and floor and ceiling, with 8" being better (reduced energy usage).  In a DH kiln, you will use over 1/3 of the energy input through the walls, floor and ceiling, so extra insulation will save energy and reduce the size of the power plant.  Your comment about infiltration is also very important...leaks can result in huge energy losses indeed. 

Depending on fuel cost for your boiler, oftentimes, energy is too cheap to save, so the extra insulation may not be economically justified; but it is from an energy conservation viewpoint.  (Insulation does indeed cost money today, but the benefit is lower monthly costs for years to come.)

Your comment about air drying is also excellent; you save more energy by air drying first, plus the kiln can dry more lumber per year.  The profit in a kiln is really based on throughput and quality, so air drying does indeed greatly help throughput.  Poor air drying practices can cost plenty if there are quality losses however, so watch that.  Again, air drying hard maple is not a good idea, from a white color standpoint; slow air drying color can be poor. 

Incidentally, to get the core of wood up to 133 F for sterilization, it will be necessary to maintain the kiln air temperature at 150 F for as long as 24 hours, depending on lumber thickness.

UGLY TREE:  Regarding SIPs, I have seen them used.  Obviously, a thin panel is not as good as a thick panel.  The overall insulation value (R rating) would be important.  The joint connection is also very important, as a lot of heat can be lost through a metal joint.  (Analogy:  A bucket can hold lots of water, but even a small hole will soon empty the bucket.  Insulated walls, floor and roof can hold in a lot of heat, but a few small holes (metal joints for example) can quickly drain away a lot of heat.)  I think that an R=30 would be the minimum for the panel and that is with an insulated joint of some sort.  The temperature sensitivity of the glue would indeed be important, as well as of the insulation itself.
Gene - Author of articles in Sawmill & Woodlot and books: Drying Hardwood Lumber; VA Tech Solar Kiln; Sawing Edging & Trimming Hardwood Lumber. And more

xlogger

I slab up a couple red maple logs about 6 months ago into 2" and put them under a shed close to the end so they could get some air flow. Are you saying this was a bad idea?
Timberking 2000, Turbo slabber Mill, 584 Case, Bobcat 773, solar kiln, Nyle L-53 DH kiln

GeneWengert-WoodDoc

Shed air drying with good air flow is almost always a great idea.  For most species, reasonably fast drying, meaning good air flow and modest humidity, gives excellent quality in a short time.  Keeping sun and rain off the lumber is important.
Gene - Author of articles in Sawmill & Woodlot and books: Drying Hardwood Lumber; VA Tech Solar Kiln; Sawing Edging & Trimming Hardwood Lumber. And more

WDH

Unless there is very good airflow, sticker stain is a big problem with air drying maple in the South.  Supplemental fans are required to keep the air velocity up for the first few weeks.  Forum member @Yellowhammer has conducted some experiments, and has posted results here on the Forum. 
Woodmizer LT40HDD35, John Deere 2155, Kubota M5-111, Kubota L2501, Nyle L53 Dehumidification Kiln, and a passion for all things with leafs, twigs, and bark.  hamsleyhardwood.com

johnnyllama

Thanks Gene. I'm also looking into the logosol kiln system, probably the 800 model. Cost is more and electric is also more but we are thinking about a solar grid tied system for our home and shop area and the sizing of the system for tax incentives and grants is based on overall usage so we may just go that route and increase the solar sizing to include those costs. Got to look into that some more.
Turner Bandmill, NH35 tractor, Stihl & Husky misc. saws, Mini-excavator, 24" planer, 8" jointer, tilting shaper, lathe, sliding table saw, widebelt sander, Beautiful hardworking wife, 2 dogs, 2 cats, 23 llamas in training to pull logs!!!

GeneWengert-WoodDoc

Solar can be very attractive, but remember that drying of air dried lumber requires about 3 million BTU per MBF.  For a ten day cycle, that would be 300,000 BTU per day.  Solar input is about 1000 BTU per sq. ft. per day, so you would need 300 sq ft of collector per MBF.  Of course, wintertime operation would be slow and summertime would be faster.
Gene - Author of articles in Sawmill & Woodlot and books: Drying Hardwood Lumber; VA Tech Solar Kiln; Sawing Edging & Trimming Hardwood Lumber. And more

LeeB

Gene, I do believe he meant solar electric.
'98 LT40HDD/Lombardini, Case 580L, Cat D4C, JD 3032 tractor, JD 5410 tractor, Husky 346, 372 and 562XP's. Stihl MS180 and MS361, 1998 and 2006 3/4 Ton 5.9 Cummins 4x4's, 1989 Dodge D100 w/ 318, and a 1966 Chevy C60 w/ dump bed.

terrifictimbersllc

Thinking the watts and kilowatts being discussed above should be watt-hours (Wh) and kilowatt-hours (kWh). 
DJ Hoover, Terrific Timbers LLC,  Mystic CT Woodmizer Million Board Foot Club member. 2019 LT70 Super Wide 55 Yanmar,  LogRite fetching arch, WM BMS250 sharpener/BMT250 setter.  2001 F350 7.3L PSD 6 spd manual ZF 4x4 Crew Cab Long Bed

GeneWengert-WoodDoc

I should have said kWH...Yes indeed.  Thanks for pointing this out.  Corrections have been made.
Gene - Author of articles in Sawmill & Woodlot and books: Drying Hardwood Lumber; VA Tech Solar Kiln; Sawing Edging & Trimming Hardwood Lumber. And more