Started by tyb525, December 17, 2010, 09:36:49 AM

Previous topic - Next topic

0 Members and 1 Guest are viewing this topic.

tyb525

I think this is the best board for this topic.

We have a woodstove that is connected to an old brick chimney. The chimney is in great shape, it runs up beside our house and ends about 3 feet above the roof. It's always seemed to have a great draft.

However, last year we had a chimney fire. Luckily, it didn't last long and stayed within the chimney. Unfortunately, it was a windy day and it got real hot real fast, and apparently it cracked the clay liner up near the top - smoke was coming out between the bricks/mortar.

Because of that, we had some chimney guys put in a new chimney liner. It was the 8" flexibly corrugated metal stuff, which seemed awful small to me, but I'm no chimney expert. Anyways, now to my question.

Would this liner cause the stove to need much more air in order keep the fire burning with any kind of heat? Before the liner, we could fill the stove with wood, close the vents almost all the way, and it would stay lit and last pretty much until early morning. If we try to do that now, it either goes out or just smolders and doesn't produce heat. During the day when someone is at home to tend the fire (that person is me ;)) the vents have to be wide open to get decent heat, and it goes through wood almost twice as fast (I also cut the firewood).

The stove is a Dutchwest "Federal Airtight". The new liner is clean.

If any of ya'll got any DanG ideas, I'd sure appreciate them ;D
LT10G10, Stihl 038 Magnum, many woodworking tools. Currently a farm service applicator, trying to find time to saw!

doctorb

Most wood stove manufacturers rec. an 8" pipe off the back of the stove.  I think it will change little as to how your stove works.
My father once said, "This is my son who wanted to grow up and become a doctor.  So far, he's only become a doctor."

tyb525

The pipe from the stove to the wall is 8", always has been.

My thoughts are that the new liner restricts the flow, especially since the chimney is two stories, and because the liner is now corrugated, and not necessarily a straight shot all the way up (it might have a few slight curves in it because it is significantly smaller in diameter than the old clay liner). This all would reduce draft I would think.
LT10G10, Stihl 038 Magnum, many woodworking tools. Currently a farm service applicator, trying to find time to saw!

beenthere

Sounds like trying to burn wet wood.

What is the history of the wood? when cut, how long since split, species, etc. ??
south central Wisconsin
It may be that my sole purpose in life is simply to serve as a warning to others

Bill

+1

imho - having to open up the air intakes is a sign there's more restriction in the " new " chimney ( liner ) . I'm thinking the new liner doesn't " flow " as well so needs a little more air to keep things going.  As long as the wood is still the same load of nice dry stuff . . .

I'd also think it allows somewhat " cooler air " to separate the new metal liner from the original clay liner ( maybe just the corners but still ) . I think that lowers the temperature ( even just a little ) which I suppose could also " lower " the drawing power of the " new " chimney.

at least that's my $0.02 and worth every penny of it   ;D

mad murdock

I think the only way to know for sure would be to have WC readings before and after the liner replacement to know for sure if it has made a difference.  Obviously something has changed since the stove is the same before and after the chimney repair, and the only thing different is the liner.  If you have a good HVAC tech that you could pick his brain, maybe that would reveal more light on the subject?  You can google Water Column meter, and maybe figure a way to make a simple one using clear pvc flexible hose? It is pretty easy to rig up something that will give you a fairly accurate read on actual draft conditions.
Turbosawmill M6 (now M8) Warrior Ultra liteweight, Granberg Alaskan III, lots of saws-gas powered and human powered :D

tyb525

The wood is the same as we've always burned, mixed hardwoods dried at least a year.
LT10G10, Stihl 038 Magnum, many woodworking tools. Currently a farm service applicator, trying to find time to saw!

Reddog

Sounds like you need to talk to some new chimney sweeps.
I would question their install job.

SwampDonkey

Tyb, I am also wondering about that install job to. Can you see up the flu with a mirror? My uncle did some work on a kitchen flu that is on the outside of the house. Somehow a piece of metal, whether from the inside of the old flu liner or otherwise got lodged and the draft was restricted and would smoke terrible. When the draft on your stove is wide open do you get a rapid chug chug sound when the fire is flaming good? That is the sign of a good draft to me. The trouble with the outside flu is it's a lot colder than running up through the centre of the house. Of course you guys down there aren't in extreme cold like us northerners. But I've seen them outside flues with steel liners clog up near the exit, have a chunk fall down and cut off the air and turn the house into a smoke house. My uncle had that happen with a wood furnace hooked up to one.  A closed damped fire is a recipe for build up in the flu. Gotta get some heat up there. I leave my damper control on 80 degrees (thermostat controlled) to the furnace. That's half open. Of course it opens further when calling for more heat in the living space until the fire is gone out. This fall has been a mild one here, the fire has been left to go out many times. Otherwise too hot. :D

Time to throw a stick in. :)
"No amount of belief makes something a fact." James Randi

1 Thessalonians 5:21

2020 Polaris Ranger 570 to forward firewood, Husqvarna 555 XT Pro, Stihl FS560 clearing saw and continuously thinning my ground, on the side. Grow them trees. (((o)))

CX3

Just another thought here, sometimes the direction of the wind can make a big difference in the draft.  I know if we have an E/NE wind our stove does not draft well because of some large trees next to the chimney.  Its almost like the wind comes around those trees and "down" the chimney.  When the wind switches the draft is great.  Also cool damp mornings can have a big effect on the draft.  It doesnt sound like this is your case, but thought I would say what our stove does. 
John 3:16
You Better Believe It!

SwampDonkey

Yes, cold dry air draws better, more oxygen. But, don't think this is the issue here.

I would burn one of those chimney sweep logs every other month as well. They burn for 1-1/2 hours, just toss it in on low coals not on flames.
"No amount of belief makes something a fact." James Randi

1 Thessalonians 5:21

2020 Polaris Ranger 570 to forward firewood, Husqvarna 555 XT Pro, Stihl FS560 clearing saw and continuously thinning my ground, on the side. Grow them trees. (((o)))

mad murdock

That is a good tip SD.  Those chimney sweep logs do work pretty well to cut down on build up.  I too would question the liner install.  It doesn't make sense that you would have that much of a change in such a short time. My previous suggeston on measuring W/C was to find out what was really going on, if everything else "looks" ok.
Turbosawmill M6 (now M8) Warrior Ultra liteweight, Granberg Alaskan III, lots of saws-gas powered and human powered :D

tyb525

We have a damper, but since the install there has never been a time to use it. Used to be on any kind of windy day we would have to close it some to keep the fire under control. We haven't touched it this year.

SD, I know the sound you are talking about, but I don't think I have noticed that sound recently.
LT10G10, Stihl 038 Magnum, many woodworking tools. Currently a farm service applicator, trying to find time to saw!

dsgsr

If the chimney is on the outside of the house, it should be insulated. I just went through that prob.  I built an enclosure around the chimney 3/4 of the way up, would have gone a little further but had the roof pitch to contend with. First I built the framing with a 2.5" offset, (code) put 6" of fire/water proof insulation in and closed it in with plywood and covered with vinyl (same as house). It's working good so far. The metal chimney that was put in, should have been rapped with fire proof blanket. That may be your prob.

David
Northlander band mill
Kubota M59 TLB
Takeuchi TB175 Excavator
'08 Ford 550 dump
'87 International Dump
2015 Miller 325 Trailblazer Welder/Gen

Dana

I had a similar problem a few years ago. I had a chimney fire and installed the flexible stainless liner to be safe. My bigest problem was that the liner cooled the smoke down so bad that I had watery creosote dripping from the stove pipe in the house.

I was going to pour a light weight concrete around the pipe to hopefully insulate it better. I had experimented with a vermiculate portland mix that I think would have worked. I bought an outdoor woodburner before I completed the experiment.

The liner I used was dura vent and as I remember they required an insulating wrap for the outside of the pipe. Did they install one?
Grass-fed beef farmer, part time sawyer

WH_Conley

Another vote to question the install. If you know the name of the product you should be able to find installation instructions, to check if it was done right. I agree about the sound, it will tell if it is working right.

Has no bearing on your problem, but, I also had a flue fire last winter, cracked the masonry block flue and liner. Tore it out the next day and installed stainless steel insulated flue system. The old masonry flue drew pretty good. The stove is in the basement, had to have 2 elbows to hook it up. The new one is straight up, one elbow out the back of the stove. Have to leave the damper turned off or it sounds like a jet engine. Had creosote problems with the old system, not the new. If you have to do any more work on the flue you have you might check prices on the stainless. If you put it inside like SwampDonkey was talking about they are easy to hide. You also get some radiated heat from the pipe to.
Bill

tyb525

Correction, it's only 6" coming from the stove which is correct for that stove, but then the liner is also 6". The old liner was 12". I would imagine that the liner doesn't make a straight shot up the chimney - I picture it looking like a snake.

Also, no insulation was installed, but neither my mom nor I can remember the brand.

The chimney goes down to the basement, where a coal furnace used to be. The chimney installers left a T where the stove connects to the chimney, the bottom on the T is open. Could that be a factor also?
LT10G10, Stihl 038 Magnum, many woodworking tools. Currently a farm service applicator, trying to find time to saw!

SwampDonkey

Take a picture Tyb so we can see it. The connection from the stove to the flu. Is the T inside the old flu? That's so you can hook up another appliance on the other side and the bottom is open to clean the flu. Also, what about your cleanout at the bottom of the flu? Take a piece of tinfoil and hold it up to the cleanout area (when the hole is closed off) and see if the tinfoil gets sucked to the chimney wall. All mine is at the bottom is two bricks I take out to clean the soot. Some are metal plates that cover the hole.
"No amount of belief makes something a fact." James Randi

1 Thessalonians 5:21

2020 Polaris Ranger 570 to forward firewood, Husqvarna 555 XT Pro, Stihl FS560 clearing saw and continuously thinning my ground, on the side. Grow them trees. (((o)))

CX3

The bottom of the T being open would absolutely be a problem.  The draft is going to draw air from the easiest place.  In this case it is easier to draw air from an open pipe (the T) than it would be to pull air from a firebox full of wood.  Close that off. 

Also going from 12 inch down to 6 would also explain some of your problems.  That stove is not breathing like it was before.  You put a noose on its neck.
John 3:16
You Better Believe It!

SwampDonkey

Yes if it's out in the room, a problem in deed. Then I have to ask why an elbow wasn't used? I can't picture that setup, the only "T" I use is the connect a flu from the oil furnace to that of the wood furnace. An oil furnace makes almost no smoke in an efficient burner. Best set up is an incline/slope from the stove toward that flu thimble, elbow at the thimble. Want as few turns as possible and then vertical up the flu. Furnaces here recommend at least 7" pipe, but you have to go with what the stove fitting it. Yours is 6" I guess. The 12 down to a 6" I can't see as a problem because you only have volume of 6" in the stove pipe, so it could be a cannon sized flu, it's only going to draw in from a 6" stove pipe.
"No amount of belief makes something a fact." James Randi

1 Thessalonians 5:21

2020 Polaris Ranger 570 to forward firewood, Husqvarna 555 XT Pro, Stihl FS560 clearing saw and continuously thinning my ground, on the side. Grow them trees. (((o)))

WH_Conley

Pictures please. As CX3 said if that is open the stove doesn't have a chance. I am thinking that the "T" should be sideways, one straight leg hooked to the liner, the other straight leg plugged with a cap for the clean out, and the angle leg going to the stove.
Bill

SwampDonkey

Sounds like those boys were scrounging to make due if they went and done that. Something I'm not picturing. I have seen a T setup on a pipe in a shop stove, but outside the shop. And the bottom kept closed until cleaned.
"No amount of belief makes something a fact." James Randi

1 Thessalonians 5:21

2020 Polaris Ranger 570 to forward firewood, Husqvarna 555 XT Pro, Stihl FS560 clearing saw and continuously thinning my ground, on the side. Grow them trees. (((o)))

John Mc

If I'm picturing your "T" correctly, it's a sideways T. What would be the top of the T is running vertically, hooked to your flue on one end, and nothing on the other end (which is pointed straight down) The stem of the T is pointing sideways, and hooks in to your stove.

The end which is not connected to anything should certainly be capped off. Your installer screwed up big time if he did not close this off. There are a couple of reasons for using a T rather than an elbow:

  • You can remove the cap for cleaning, and brush out your chimney from below, rather than up on the roof (assuming it's high enough off the ground to get the rods in)
  • The stub end of the T makes a place for any crud/cinders/creosote to drop into, rather than collecting in the elbow or the top of the stove.
  • If sweeping the chimney from above, you can open the cap on the stub end, tape a trash bag around it, and anything swept out will fall straight down into the bag... you don't have to disconnect the stove

Unlike others here, I don't think the switch from 12" flue to a 6" would cause a problem with a stove designed for a 6" flue (as yours seems to be, judging from its 6" exit. In fact, an oversize flue can cause problems with draw and with creosote formation, since it will run cooler.

Like others, I do question the installation. If they just snaked a bare 6" liner down a 12" flue without and form of insulation, or something to take up the airspace, that liner is going to run cold -- especially if they did not seal off the extra opening at the top between the liner and the original 12" flue.

One other thing to check: is it possible the fire damage any part of your stove, or that crud from the fire dropped down the flue and is partially blocking the exhaust at the top of your stove? My stove exits straight up into the chimney (built to look like a fireplace, with a stove sitting in it). One year I did have some problems with stuff flaking off my flue, falling down into the stove and partially blocking the exhaust. I had to crank the air open to get it to burn at all, and it was still a pain in the neck. Disconnecting the stove and vacuuming out the opening made a big difference. (I would think a competent installer would have checked for debris in the top of the stove after a chimney fire, if the flue connection was such that it could have made it back into the stove.)
If the only tool you have is a hammer, you tend to see every problem as a nail.   - Abraham Maslow

SwampDonkey

I have a clean out hole in my flu to brush out the flu. I don't try to clean a flu from a stove pipe. I remove my pipes monthly to clean them with a brush. It would take some snaking to get a flu brush around all them turns. My way the brush goes straight up from the bottom. Also, make sure your not using a steel brush in that new metal liner.
"No amount of belief makes something a fact." James Randi

1 Thessalonians 5:21

2020 Polaris Ranger 570 to forward firewood, Husqvarna 555 XT Pro, Stihl FS560 clearing saw and continuously thinning my ground, on the side. Grow them trees. (((o)))

tyb525

The "T" is vertical - it is inside the chimney.

The bottom the T is open. The chimney men said that was to allow creosote to fall to the bottom, where there is a metal cleanout door.

The flu connection from the stove to the chimney is all original, it's been there since the stove was installed in the late 80's, however we take it apart and clean it every year. We also clean inside the stove. We clean the chimney with a brush-and-rope system: brush with rope on both ends, person at top, person at bottom. Pull all the way up, then all the way down multiple times. However, we haven't cleaned the new liner yet, we had the same guys clean it when we noticed that it wasn't performing the same.

It would make sense that smaller flu would increase the draft, especially if it is what the stove is designed for. However, considering the chimney is 2 stories, it seems like that would be too small a pipe for the volume of smoke. The old 12" worked much better.





LT10G10, Stihl 038 Magnum, many woodworking tools. Currently a farm service applicator, trying to find time to saw!

SwampDonkey

That's what I thought you were talking about. I couldn't imagine it any other way. That is fine. It would be no different than the old clay liner system.  I think the trouble is air flow around the outside of that new liner, between it and the flu walls. Creasote buildup on those cool walls. See if they insulated it down to the thimble by the stove pipe.
"No amount of belief makes something a fact." James Randi

1 Thessalonians 5:21

2020 Polaris Ranger 570 to forward firewood, Husqvarna 555 XT Pro, Stihl FS560 clearing saw and continuously thinning my ground, on the side. Grow them trees. (((o)))

Holmes

John Mc is correct the open end must be capped. The flue is sucking air from everplace except the stove , the path of least resistance is the open tee.
Think like a farmer.

tyb525

They didn't insulate it at all, which seems to be the problem, along with the open T. :-\ We'll be contacting them I'm sure.
LT10G10, Stihl 038 Magnum, many woodworking tools. Currently a farm service applicator, trying to find time to saw!

SwampDonkey

Another question here, is your flu higher than the peak of the house? The flu has to be the tallest structure for good draft.

Maybe the top plate on the flu up top isn't installed properly.

Here is a site to have a look at with chimney liners.

http://askthechimneysweep.com/2009/08/installing-a-flexible-stainless-steel-chimney-liner
"No amount of belief makes something a fact." James Randi

1 Thessalonians 5:21

2020 Polaris Ranger 570 to forward firewood, Husqvarna 555 XT Pro, Stihl FS560 clearing saw and continuously thinning my ground, on the side. Grow them trees. (((o)))

Don_Papenburg

Doubling the dia. of pipe increases the volume four times .  a larger pipe will slow the velosity of the gasses.  so if the stove is 6" the flue also should be 6" no more than 8" .

I think that the open bottom T is making the draft problem .  How hard will it be to plug that hole .  Basicly that would be cutting you stove gas exhaust draft in half .  The hot gas is pulling the cold air up with it .  50/50 mix? maybe .  so that drops stove volume almost 50% .
But then you have the cooling effect also . that drops the speed of the flue gas as it cools.  that might be putting you at only 75% of normal volume.
Frick saw mill  '58   820 John Deere power. Diamond T trucks

SwampDonkey

I don't know how your going to clean that flu when bottom is capped off and how the heck are you going to deal with taking it off to clean the flu? What happens when that bottom end gets full of creasote and soot? I think insulating the liner, checking the cap to see that it's sealed on there, and also flu height if it isn't above the peak, which at this point I don't know.
"No amount of belief makes something a fact." James Randi

1 Thessalonians 5:21

2020 Polaris Ranger 570 to forward firewood, Husqvarna 555 XT Pro, Stihl FS560 clearing saw and continuously thinning my ground, on the side. Grow them trees. (((o)))

Holmes

Quote from: SwampDonkey on December 18, 2010, 12:10:53 AM
I don't know how your going to clean that flu when bottom is capped off and how the heck are you going to deal with taking it off to clean the flu? What happens when that bottom end gets full of creasote and soot? I think insulating the liner, checking the cap to see that it's sealed on there, and also flu height if it isn't above the peak, which at this point I don't know.
The bottom of the tee could be run to the cleanout door then capped. The top of the old flue shall be sealed off with metal and the liner shall pass thru it. Now the space in the chimney between  the liner and the flue can act as an insulated chamber. Insulating the pipe would be better ,but the old flue must be capped off. You still need to cap the open tee. Holmes
Think like a farmer.

SwampDonkey

My understanding with the top sealed/caulked as it should be, is it can't suck air down and in the bottom of that open end of the T. And that section into the thimble of the flu to the stovepipe needs sealing off so it don't suck air in from the room from that open end.
"No amount of belief makes something a fact." James Randi

1 Thessalonians 5:21

2020 Polaris Ranger 570 to forward firewood, Husqvarna 555 XT Pro, Stihl FS560 clearing saw and continuously thinning my ground, on the side. Grow them trees. (((o)))

Holmes

Quote from: SwampDonkey on December 18, 2010, 07:26:23 AM
My understanding with the top sealed/caulked as it should be, is it can't suck air down and in the bottom of that open end of the T. And that section into the thimble of the flu to the stovepipe needs sealing off so it don't suck air in from the room from that open end.
That is correct.I would still like to see the tee capped off. The old flue could have air getting into it thru fractures, the cleanout door , and around the flue pipe. Holmes
Think like a farmer.

beenthere

Holmes
You have the right solution to solve the problem.
south central Wisconsin
It may be that my sole purpose in life is simply to serve as a warning to others

John Mc

I still may not be picturing this correctly. Your T is inside the chimney, allowing the creosote to drop to the bottom of the cleanout, where you can reach it by opening the door?

This might work OK without capping the T, if the door seals well when closed, and all other openings are blocked (the top of the chimney, the thimble where it connects to the stove). Basically, you don't want to draw any air in through the open end of the T. You can do this by capping off the T, or blocking off any sources of air getting to the open end of the T.

However, as I think about your situation further, I don't know how you can block off the other air sources. The obvious ones are fairly straightforward - the top of the chimney between the old 12" flue and the new liner, the thimble, and the clean-out door. The problem is that the new liner was put in because there were problems with the old one after the chimney fire. The old 12" one most likely has some leaks somewhere along its length (otherwise, why put in a new liner?). You are not going to be able to plug those. This will cause 2 problems: 1) it allows in air to the space between the 12" and the new 6" flues, providing a source of air to the open end of your T. and 2) the cooler air being drawn in through the cracks in the chimney/12" flue will cool your uninsulated 6" flue, causeing further draft problems and creosote formation.

All this leave me thinking you do need to cap that open T. Perhaps you can extend it downward so the cap is easily reachable from the clean-out door? This would make it easy to remove when cleaning the flue. However, that this is probably just a start towards resolving the problem -- though it may be a good start.

I have to wonder if the guys who installed this had any idea what they were doing? An uninsulated metal flue inside a much larger flue with multiple paths for air to enter the space between the two, and an open T into the new flue??

One thought: When my parents renovated the kitchen in an old farmhouse after a kitchen fire, they decided to add a small fireplace. They wanted to tap into an old, unused chimney. The flue was in bad shape. The could not fit a round flue of the size required into the opening (they had more than enough cross sectional area, but it was in the wrong shape). They found someone who put something down the chimney as a form, then poured some sort of material (castable?) to fill the gap between the form and the old flue. Basically, they poured a new flue liner in place. I wish I could be more specific, but I wasn't around when this was done. It sounds as though something similar might work in your situation?

John Mc

If the only tool you have is a hammer, you tend to see every problem as a nail.   - Abraham Maslow

SwampDonkey

It will help the draft with that cap, no question. I just hope you can extend that T to the cleanout and then be able to get it off to clean when the creasote seals it nice and tight. I don't know that  a little air through the masonry is all that big a deal, but it may prove to be.
"No amount of belief makes something a fact." James Randi

1 Thessalonians 5:21

2020 Polaris Ranger 570 to forward firewood, Husqvarna 555 XT Pro, Stihl FS560 clearing saw and continuously thinning my ground, on the side. Grow them trees. (((o)))

tyb525

SD, the top of the chimney is 3 feet higher than anything else on the house.

Extending the T down to the cleanout door should work, and I believe it would be accessible that way. I'm pretty sure I could make a simple cap that would be easily removable, and a cap for the top to seal it off, also.
LT10G10, Stihl 038 Magnum, many woodworking tools. Currently a farm service applicator, trying to find time to saw!

SwampDonkey

Good on you Tyb, because I didn't know how easy it was going to be to add an extension on and cap the bottom by the cleanout. I wouldn't be able to do it through my cleanout and most I've seen don't have a very big opening to work from. You should be able to get a cap for the top from the stove store and make sure it's sealed onto the old flu brick with some caulking. Three feet is lots of height. I didn't know if that was part of the problem because you had a huge 12" flu there for air before, now 6".
"No amount of belief makes something a fact." James Randi

1 Thessalonians 5:21

2020 Polaris Ranger 570 to forward firewood, Husqvarna 555 XT Pro, Stihl FS560 clearing saw and continuously thinning my ground, on the side. Grow them trees. (((o)))

Holmes

 Tyb It sounds like your chimney guys have a lack of experience.  A cover for the top of the flue  and a cap for the new liner should have come with the liner kit. More important is to find out if the liner is stainless steel, it is supposed to be, no it has to be SS. If it is aluminum it will burn up with a chimney fire. Holmes
Think like a farmer.

SwampDonkey

Holmes I think it was the flexible stainless, Tyb will know.
"No amount of belief makes something a fact." James Randi

1 Thessalonians 5:21

2020 Polaris Ranger 570 to forward firewood, Husqvarna 555 XT Pro, Stihl FS560 clearing saw and continuously thinning my ground, on the side. Grow them trees. (((o)))

tyb525

Yeah it is stainless steel, I have a scrap piece a few feet long sitting in the barn. If it was aluminum, I'd be about ready to sue those guys and reline it myself :D

Thanks for your help guys, I knew one of you a whole bunch of you would have some good knowledge on the subject :)
LT10G10, Stihl 038 Magnum, many woodworking tools. Currently a farm service applicator, trying to find time to saw!

Handy Andy

  I haven't been with this thread the whole time, just read through some of it yesterday, but reminded me of building my house. I built the house, but hired a mason to lay brick and build my chimney, for wood stove.  I told the guy while he was doing the chimney, I'd like to have the gap between the liner and the block and bricks filled in solid, and he said what with?, so I just started carrying 5 gallon buckets of fill sand over, and putting the bucket on the scaffold.  Well, he just dumped them in, and my chimney is filled right to the top with sand.  Wouldn't have to worry about a chimney fire if you had it filled with sand, would you?  Wonder why you couldn't just knock a hole in the top of the chimney where it is sealed up with concrete and dump sand down into it till you get  it filled in? And of course, fill the top in with concrete.  Then you could just take that nasty restricting pipe out.
My name's Jim, I like wood.

beenthere

I don't think I would want the weight and the pressure of a chimney filled with sand (around the liner).
I think there would be too much outward load on the chimney brick and block. In time, I think it will settle and seek a way out.

But hopefully didn't happen and never will. :)
south central Wisconsin
It may be that my sole purpose in life is simply to serve as a warning to others

John Mc

If I'm following the OP's description correctly, that sand would just flow down and fill up his cleanout as well. Might be OK on a chimney & installation designed with that in mind, but I'm not sure how well that would work here.
If the only tool you have is a hammer, you tend to see every problem as a nail.   - Abraham Maslow

Handy Andy

  My chimney has a cleanout at the basement floor, the flue liner is sitting on 4" block up to where the stove hooks onto the liner, and always thought I'd get a bit of sand leaking into it, but never have. It's 30 years old now.
My name's Jim, I like wood.