TimberKing Sawmills



Please visit this sponsor

The Largest Inventory of Used Chainsaw Parts in the World

Toll Free 1-800-582-0470

LogRite Tools

Lucas Sawmills

Forest Products Industry Insurance

Norwood Industries Inc.

Eggimann Motor and Equipment Sales Inc.

Sawmill & Woodlot Magazine

Wood-Mizer Band Blades

Carolina Machinery Sales is a machinery dealer that specializes in the Wood Processing Industry.

Wood Processing equpment. Splitters, Processors, Conveyors

Your source for Portable Sawmills, Edgers, Resaws, Sharpeners, Setters, Bandsaw Blades and Sawmill Parts

Portable Sawmill and Planers Made by Logosol.

EZ Boardwalk Sawmills. More Saw For Less Money!

STIHLDealers.com sponsored by Northeast STIHL

Lawn-Gardening-Tools.com

Hutto Wood Products

Woodland Sawmills

Margeson Insurance

Forestry Forum Tool Box

Author Topic: solar questions, plans for expansion  (Read 3554 times)

0 Members and 2 Guests are viewing this topic.

Offline OlJarhead

  • Full Member x2
  • ***
  • Posts: 175
  • Age: 46
  • Location: Washington State
  • Gender: Male
    • Team SEWA
Re: solar questions, plans for expansion
« Reply #20 on: January 18, 2011, 08:15:51 pm »
Hmmmm just reread your post and it looks like your going MUCH MUCH bigger then I was thinking when I first breezed the post...sorry, seems my post doesn't address what your doing at all.

I'd love the Outback stuff etc but the $$$ I'd rather spend on mills and such :D
Cabin building powered by A.C.T.

Offline maple flats

  • Senior Member x2
  • *****
  • Posts: 1213
  • Age: 65
  • Location: Oneida, NY
  • Gender: Male
  • Life is what you make it!
Re: solar questions, plans for expansion
« Reply #21 on: June 10, 2011, 12:50:50 pm »
update. My system is now fully functional. I have 740 watts of array, feeding in series to a FX80 charge controller. Then it charges a 48V battery bank in the form of 8 x T125 Trojan batteries. Then the power feeds thru a DC safety switch and into my XW6048 inverter. Also tied into the inverter is a 6000 watt generator. The inverter matches to wave form from the gen so they play well together. From here I go to a AC main switch and to the AC panel which then distributes power to the sugarhouse. I also run a 120 breaker to power the 5th wheel camper set up about 140' from the sugarhouse, via an 8 ga cable. I can run everything I need except the AC on just solar/batteries, but for AC I need to start the genny.
My next step is to order 4 more panels and the racking needed to add another 740 watts to my array. Everything else is ready to accept the panels.
This system can handle 7 sets x 740 watts and the only change I'll need is the cables from the charge controller to the batteries will need to be heavier after 3 sets. Also, when these batteries need replacing I will get a much larger battery bank for more storage, have not decided if it will be several strings of the same Trojans or maybe some Rolls Surrette or another choice.
I am not on the grid, not sure if I ever will.
logging small time for years but just learning how, with a Forest stewardship plan, 2 compact Ford 4x4 tractors, 3point log arch, 8000# class excavator, lifts 2500# and sets logs on mill precisely where needed,  Peterson ATS upgraded to WPF mill, sugar maple/maple syrup a hobby gone amuck.

Offline OlJarhead

  • Full Member x2
  • ***
  • Posts: 175
  • Age: 46
  • Location: Washington State
  • Gender: Male
    • Team SEWA
Re: solar questions, plans for expansion
« Reply #22 on: June 20, 2011, 10:47:21 pm »
update. My system is not fully functional. I have 740 watts of array, feeding in series to a FX80 charge controller. Then it charges a 48V battery bank in the form of 8 x T125 Trojan batteries. Then the power feeds thru a DC safety switch and into my XW6048 inverter. Also tied into the inverter is a 6000 watt generator. The inverter matches to wave form from the gen so they play well together. From here I go to a AC main switch and to the AC panel which then distributes power to the sugarhouse. I also run a 120 breaker to power the 5th wheel camper set up about 140' from the sugarhouse, via an 8 ga cable. I can run everything I need except the AC on just solar/batteries, but for AC I need to start the genny.
My next step is to order 4 more panels and the racking needed to add another 740 watts to my array. Everything else is ready to accept the panels.
This system can handle 7 sets x 740 watts and the only change I'll need is the cables from the charge controller to the batteries will need to be heavier after 3 sets. Also, when these batteries need replacing I will get a much larger battery bank for more storage, have not decided if it will be several strings of the same Trojans or maybe some Rolls Surrette or another choice.
I am not on the grid, not sure if I ever will.

Wow!  I'm jealous!  I'm only running 880ah using Costco GCB's right now with 615 watts of solar panels running into a Morningstar Tri-Star MPPT (60a) controller and an AIM 2500 watt inverter -- I've also got a 3000 watt generator and a 750 watt Iota battery charger in case the sun doesn't come out long enough....off-grid cabin but I wish I had MORE POWER! :D  It's cubic dollars though isn't it?
Cabin building powered by A.C.T.

Offline logman

  • Full Member x2
  • ***
  • Posts: 167
  • Age: 54
  • Location: Fleetwood, NC
  • Gender: Male
  • I need to edit my profile!
Re: solar questions, plans for expansion
« Reply #23 on: June 21, 2011, 06:31:25 am »
I am getting ready to order my panels and inverter.  I am getting a XW 4024 inverter and was told I needed the MPPT charge controller which is over 500.00.  The place I am getting it from told me the C series controllers wouldn't work with the inverter.  I was going to order a MorningStar controller.  No problems Maple Flats with your controller and inverter?
LT40HD, 12' ext, 5105 JD tractor

Offline JSNH

  • Full Member x2
  • ***
  • Posts: 142
  • Age: 48
  • Location: Deering New Hampshire
  • Lane circular mill
Re: solar questions, plans for expansion
« Reply #24 on: June 21, 2011, 12:38:04 pm »
No one needs a MPPT charge controler. I used a c40 with my starter set of panels 8- 200watt ones. The MPPT allows you to run higher voltages from  the panels so you loose less in the wire and can run smaller wire. It also pulls more power out of the panels. I started with two stings of 4- 200 watt panels and a used c40. I have expanded to three strings of 5- 200 watt panels and now have a outback mx 60 MPPT controler. You have to run the numbers a MPPT may be worth the $. but then again with solar at $1.50 a watt depending on how large of a system an extra panel may make more sense.

Offline maple flats

  • Senior Member x2
  • *****
  • Posts: 1213
  • Age: 65
  • Location: Oneida, NY
  • Gender: Male
  • Life is what you make it!
Re: solar questions, plans for expansion
« Reply #25 on: June 21, 2011, 07:02:28 pm »
I have no problems with my equipment combination. I went MPPT because of the distance from panels to the sugarhouse (240'). I am running 96V nominal but when the winter temps and in the sun it makes over 120V quite often. If I connected a 5th panel in series the charge controller would shut off at cold temps in good sun and waste the energy when I might need it the most. A MPPT controller actually gives far higher efficiency than a PWM (pulse width modulated) controller. My controller is in the upper 90's percentile for efficiency, I'd need to read it again but my inverter and controller were each at 95% or higher, one was 96% and the other at 97%. This gives me the highest possible. Now, at best battery conversion is much lower. When I use the power as it is being generated I get very good efficiencies but by the characteristics of batteries, I get less use from my stored energy. When I need more power I start the generator. Then the inverter syncrinizes the wave form. the gen power is priority, and surplus charges the batteries. If I draw a load too high for the generator it is supplemented from the batteries.
This is still a learning experience.
One thing really surprised me back in March sometime, we had a "super moon" and I noticed the moon was charging the batteries.
logging small time for years but just learning how, with a Forest stewardship plan, 2 compact Ford 4x4 tractors, 3point log arch, 8000# class excavator, lifts 2500# and sets logs on mill precisely where needed,  Peterson ATS upgraded to WPF mill, sugar maple/maple syrup a hobby gone amuck.

Offline OlJarhead

  • Full Member x2
  • ***
  • Posts: 175
  • Age: 46
  • Location: Washington State
  • Gender: Male
    • Team SEWA
Re: solar questions, plans for expansion
« Reply #26 on: June 22, 2011, 01:11:08 am »
I have no problems with my equipment combination. I went MPPT because of the distance from panels to the sugarhouse (240'). I am running 96V nominal but when the winter temps and in the sun it makes over 120V quite often. If I connected a 5th panel in series the charge controller would shut off at cold temps in good sun and waste the energy when I might need it the most. A MPPT controller actually gives far higher efficiency than a PWM (pulse width modulated) controller. My controller is in the upper 90's percentile for efficiency, I'd need to read it again but my inverter and controller were each at 95% or higher, one was 96% and the other at 97%. This gives me the highest possible. Now, at best battery conversion is much lower. When I use the power as it is being generated I get very good efficiencies but by the characteristics of batteries, I get less use from my stored energy. When I need more power I start the generator. Then the inverter syncrinizes the wave form. the gen power is priority, and surplus charges the batteries. If I draw a load too high for the generator it is supplemented from the batteries.
This is still a learning experience.
One thing really surprised me back in March sometime, we had a "super moon" and I noticed the moon was charging the batteries.

Funny you mentioned that -- I get a lot of charging out of my setup when the sun is hiding behind trees or clouds and even a decent trickle when it isn't even fully up above the horizon.  Seems any light in the sky gives me something.

On the other hand I've not seen the panels give me the power they are rated at.  So far the most I've seen is 299 watts but that may not mean anything as I've yet to see them perform in full sun directly on the panels with a need to produce...we will soon see that though ;)

I'm always amazed at how the MPPT controller adjusts the voltage and amps to meet the needs of the system too...amazing.
Cabin building powered by A.C.T.

Offline OlJarhead

  • Full Member x2
  • ***
  • Posts: 175
  • Age: 46
  • Location: Washington State
  • Gender: Male
    • Team SEWA
Re: solar questions, plans for expansion
« Reply #27 on: June 22, 2011, 01:13:41 am »
I should add that I have a Xantrex C40 but swapped it out for the Morningstar MPPT because I was was running 54vdc from the panels (actually as high as 67vdc) and the C40 isn't designed for that kind of use so I was wasting a lot of charging power.

However, I fail to see how it would impact an inverter??  The charge controller charges the batteries, the inverter draws power from the batteries....shouldn't matter what controller is being used and for that matter NO controller is required to run an inverter (you could just plug it into the batteries and use an iota charger and a generator to keep them topped up if you didn't have solar).
Cabin building powered by A.C.T.

Offline logman

  • Full Member x2
  • ***
  • Posts: 167
  • Age: 54
  • Location: Fleetwood, NC
  • Gender: Male
  • I need to edit my profile!
Re: solar questions, plans for expansion
« Reply #28 on: June 22, 2011, 05:58:16 am »
I think the main reason the company said a C series controller wouldn't work is that it wouldn't communicate with the inverter. 
LT40HD, 12' ext, 5105 JD tractor

Offline maple flats

  • Senior Member x2
  • *****
  • Posts: 1213
  • Age: 65
  • Location: Oneida, NY
  • Gender: Male
  • Life is what you make it!
Re: solar questions, plans for expansion
« Reply #29 on: June 22, 2011, 06:19:03 am »
My FX80 does not communicate with the controller. It works fine. It might tweak the efficiency if it did however.
logging small time for years but just learning how, with a Forest stewardship plan, 2 compact Ford 4x4 tractors, 3point log arch, 8000# class excavator, lifts 2500# and sets logs on mill precisely where needed,  Peterson ATS upgraded to WPF mill, sugar maple/maple syrup a hobby gone amuck.

Offline maple flats

  • Senior Member x2
  • *****
  • Posts: 1213
  • Age: 65
  • Location: Oneida, NY
  • Gender: Male
  • Life is what you make it!
Re: solar questions, plans for expansion
« Reply #30 on: August 30, 2011, 05:38:12 pm »
Update. I have now ordered my next 4 panels. When connected they will now total 1520 watts.
The main reason to use higher voltage inverters and array strings is max power potential. For example my FX80 controller will handle 80 amps and 80 x 48V is far more energy than 80A x 12V. The controller will run anything from a 12v, 24v, 36v, 48v or 60v battery bank and can accept power in up to 150V. There was not good choice for a 60V inverter so I chose the XW 6048 which is grid capable if I go that way. It is 6000 watt max continuous at 48v nominal voltage in. When I get bigger, I can interconnect up to 3 such inverters. At present my weak link is my battery bank. I am still using my old battery bank from my first solar endeavor of 300 watts. Since batteries of differing ages should not be mixed I will just wait until the first bank needs replacing. The old ones are only 3 yrs old When I do replace the batteries I will decide which to use but it will still be a 48v bank. Just the AH will be far larger. I also want it to be 1 string so the batteries will be huge. I have looked at some over half a ton and one over a ton. No decision yet. I can set batteries up to about 2500# and lift them into place using my excavator, but I would stay a safe margin under that so nothing goes wrong when placing them. Using such an undersized battery bank I will never get the typical 7 yrs life expectancy for Trojan 6V,  240 AH FLA batteries. In fact I started with a 24v inverter of low quality and moved up to the XW6048 less than a year later and added 4 more batteries, so I have 2 different ages now. This alone will shorten the battery bank's life.
logging small time for years but just learning how, with a Forest stewardship plan, 2 compact Ford 4x4 tractors, 3point log arch, 8000# class excavator, lifts 2500# and sets logs on mill precisely where needed,  Peterson ATS upgraded to WPF mill, sugar maple/maple syrup a hobby gone amuck.

 