TimberKing Sawmills



Please visit this sponsor

The Largest Inventory of Used Chainsaw Parts in the World

Toll Free 1-800-582-0470

LogRite Tools

Lucas Sawmills

Forest Products Industry Insurance

Norwood Industries Inc.

Eggimann Motor and Equipment Sales Inc.

Sawmill & Woodlot Magazine

Wood-Mizer Band Blades

Carolina Machinery Sales is a machinery dealer that specializes in the Wood Processing Industry.

Wood Processing equpment. Splitters, Processors, Conveyors

Your source for Portable Sawmills, Edgers, Resaws, Sharpeners, Setters, Bandsaw Blades and Sawmill Parts

Portable Sawmill and Planers Made by Logosol.

EZ Boardwalk Sawmills. More Saw For Less Money!

STIHLDealers.com sponsored by Northeast STIHL

Lawn-Gardening-Tools.com

Hutto Wood Products

Woodland Sawmills

Margeson Insurance

Forestry Forum Tool Box

Author Topic: Heat Exchanger Hook-up  (Read 2962 times)

0 Members and 1 Guest are viewing this topic.

Offline Tim Crowley

  • member
  • *
  • Posts: 26
  • Age: 52
  • Location: Rochester, Vermont
  • Gender: Male
Heat Exchanger Hook-up
« on: December 09, 2009, 11:40:26 am »
Folks, I've been operating my eclassic for about 5 months now, but it's being tested in Vermont temps. now.  Wanted to ask this question:  I've got a 50 plate heat exchanger into the bottom of which my line-in is connected.  Said another way, the water from the outside boiler is connected to the bottom of the heat exchanger, then comes out the top.  Is that the right hook-up, or am I missing something?  I've read a thread on this on the forum, but I can't seem to find it.  Thoughts?  Tim

Offline beenthere

  • Senior Member x2
  • *****
  • Posts: 14171
  • Location: Southern Wisconsin
  • Gender: Male
  • EIEIO
Re: Heat Exchanger Hook-up
« Reply #1 on: December 09, 2009, 11:46:31 am »
Seems the hot from the boiler would come in the top of the HE and the cooled water would exit the bottom.
Edit:  Upon closer look at the link I see that the hot water supply does come in at the bottom of the HE and returns out the top. So Tim, agree yours is right. Sorry for the confusion I added.  ::) ::)

When heating the water like in the wood fired boiler, the cold would come in the bottom and the hot out the top.

The house loop (if hydronic), the return water would come to the heat exchanger at the bottom and the warmer water out the top.
Make sense?

This was discussed recently (haven't found the thread) and the thought was along these lines. There were pics or drawings of how it should be.

This one might help.
http://www.centralboiler.com/forcedAirDet.html
south central Wisconsin
 It may be that my sole purpose in life is simply to serve as a warning to others

Offline Tim Crowley

  • member
  • *
  • Posts: 26
  • Age: 52
  • Location: Rochester, Vermont
  • Gender: Male
Re: Heat Exchanger Hook-up
« Reply #2 on: December 09, 2009, 11:59:30 am »
Thanks, beenthere.  Could someone help us find that thread/post as I'd like to get this corrected if it's not hooked-up right.  I just want to make sure I'm maximizing the boiler's potential and not selling its ability short for something like that.  The eclassic is serving a System 2000 boiler that provides hot air to half the house and baseboard to the other half (large old farmhouse).  What I'm finding is that the heat exchanger in the plenum "takes" the majority of the heat from the OB's water, leaving water that's not the 180 degrees that the baseboard needs to function at its best.  Does this make sense?  When I turn off the air heat, the temp. in the System 2000 boiler rises, thus serving the baseboard the temps it needs.  Hmmm . . .
Tim

Offline Jeff

  • Lead Administrator
  • Administrator
  • *****
  • Posts: 33562
  • Age: 50
  • Location: Harrison MI
  • Gender: Male
    • THEE Forestry Forum
Re: Heat Exchanger Hook-up
« Reply #3 on: December 09, 2009, 12:11:07 pm »
A quick call to central boiler might be your best bet.
The farther backward you can look, the farther forward you are likely to see. Winston Churchill.
Forestry Forum Founder and Chief Bottle Washer.

Offline red oaks lumber

  • Senior Member x2
  • *****
  • Posts: 1151
  • Age: 50
  • Location: spooner, wisconsin
  • Gender: Male
Re: Heat Exchanger Hook-up
« Reply #4 on: December 09, 2009, 01:05:55 pm »
you need a bigger circulating pump, water is moving to slow allowing the h.ec. to blow off to much heat as it goes thru , that is a good problem to have
i know nothing related to wood

Offline Tim Crowley

  • member
  • *
  • Posts: 26
  • Age: 52
  • Location: Rochester, Vermont
  • Gender: Male
Re: Heat Exchanger Hook-up
« Reply #5 on: December 09, 2009, 01:17:48 pm »
Interesting "problem" to have, huh.  When the hot air side stops calling and the fan shuts off, etc, then the inside boiler temp. goes to max (180+) from 140.  Then, the baseboard seems to have enough to do what IT was designed to do, radiate the heat.  Are you suggesting that the water that's circulating to the plenum in the hot air part of the furnace is moving too slow?

Tim

Offline irallen

  • member
  • *
  • Posts: 9
  • Location: Northern Vermont
Re: Heat Exchanger Hook-up
« Reply #6 on: December 09, 2009, 01:53:53 pm »
You have the correct hookup.

Offline Tim Crowley

  • member
  • *
  • Posts: 26
  • Age: 52
  • Location: Rochester, Vermont
  • Gender: Male
Re: Heat Exchanger Hook-up
« Reply #7 on: December 09, 2009, 02:04:39 pm »
Irallen, when you say I have the correct hook-up, are you saying that the water line from the boiler should be hooked-up to the bottom of the heat exchanger?

Tim

Offline SPIKER

  • Senior Member x2
  • *****
  • Posts: 1268
  • Location: Ohio Ashland County
  • Gender: Male
  • I'm new!
Re: Heat Exchanger Hook-up
« Reply #8 on: December 09, 2009, 02:24:39 pm »
you want to make sure that any AIR that is trapped can leave the heat exchanger, that means the EXIT should be at the top so no bubble can form/set.   If you plumb water in at the top the air an become un-entrapped in the exchanger and steam / air will not be able to get out leaving bubbling sounds coming from it...

You can set the baseboard heaters to take heat first? feed them then the furnace air circulatory?   This would make sure you have HOT water at the baseboards and that also means when they are all on and pulling hot water the heat exchanger in the air duct will not have as much HEAT available (if you are firing the air mover/furnace up or down stream in extreme conditions the cooler water will draw heat out of it unless the heat exchanger is in the return ducting...


Mark
I'm looking for help all the shrinks have given up on me :o

Offline Tim Crowley

  • member
  • *
  • Posts: 26
  • Age: 52
  • Location: Rochester, Vermont
  • Gender: Male
Re: Heat Exchanger Hook-up
« Reply #9 on: December 09, 2009, 02:40:18 pm »
Mark,

Wow!!  I was actually wondering about that possibility (giving the baseboard the hottest water first)!!  Didn't think it was possible.  What (generally) does that involve?  Is it a valve of some sort, replumbing in a major or minor way?  Some simple or complicated redirection?  My plumber did say a couple of weeks ago when I was concerned about the baseboard not gaining the heat it should, that, by all accounts, the heat exhanger for the air system was "certainly doing its job taking all the heat it could from the OB water."  He did check for air in the baseboard system, just to be sure.  None there, really.  He suggested running a couple of flexible ducts to that main living room to "assist" the baseboard.  But I got to thinking, now that the temps. are giving me a truer picture of things, that one half of the system was certainly robbing the other, it seemed.  Tell me more!!  Tell me more!! ::)

Thanks, Mark.   

Offline woodmills1

  • Senior Member x2
  • *****
  • Posts: 4173
  • Age: 60
  • Location: Hudson, NH
  • Gender: Male
  • the truth shall set you free
Re: Heat Exchanger Hook-up
« Reply #10 on: December 09, 2009, 04:40:14 pm »
I wonder if you put the baseboard first will they rob enough heat so that the air will be too cool?
James Mills    Lovely wife   collect old tools  vaccuming fool  36 bd ft per hour
 oak paper cutter,   apple jacks   ebonic yooper rapper nauga seller, Blue Ox? its not fast, 2 cat family,  LT70 and edger, 375 bd ft/hr, we like Bob, did I say free heat machine no oil 7 years

Offline beenthere

  • Senior Member x2
  • *****
  • Posts: 14171
  • Location: Southern Wisconsin
  • Gender: Male
  • EIEIO
Re: Heat Exchanger Hook-up
« Reply #11 on: December 09, 2009, 05:28:37 pm »
south central Wisconsin
 It may be that my sole purpose in life is simply to serve as a warning to others

Offline red oaks lumber

  • Senior Member x2
  • *****
  • Posts: 1151
  • Age: 50
  • Location: spooner, wisconsin
  • Gender: Male
Re: Heat Exchanger Hook-up
« Reply #12 on: December 09, 2009, 07:27:53 pm »
put in a bigger pump, no need to replumb everything. if your water temp coming back out of the heatechanger is cool to the touch put in a bigger pump(more g.p.m.) horizontal heat ec. infeed line on the bottom return line on top..... need more heat use a bigger pump, your not airlocked if your getting heat the problem is ... get a bigger pump
 been there done that!!
i know nothing related to wood

Offline red oaks lumber

  • Senior Member x2
  • *****
  • Posts: 1151
  • Age: 50
  • Location: spooner, wisconsin
  • Gender: Male
Re: Heat Exchanger Hook-up
« Reply #13 on: December 09, 2009, 07:29:26 pm »
here is an idea.. put in a bigger pump
i know nothing related to wood

Offline maple flats

  • Senior Member x2
  • *****
  • Posts: 1213
  • Age: 65
  • Location: Oneida, NY
  • Gender: Male
  • Life is what you make it!
Re: Heat Exchanger Hook-up
« Reply #14 on: December 09, 2009, 09:13:14 pm »
Not sure about the hookup on that but when I sold and installed similar untis often times more than 1 zone was called for. This can be done a couple of different ways. You will need a thermostat for each zone. You can split the flow in a manifold and have a pump for each or you can use 1 pump and zone valves. You will need check valves to make sure the hot water comes from the boiler and not back fed from another zone. Either way will give you fully hot water to each. You may need a bigger pump if the flow is not great enough because you likely don't want to add a new line from the boiler. Even a 3/4" line with a higher flow pump will move a lot of BTU's, 1" is even better. If you just go through the baseboards first you may starve the heat exchanger for needed BTU's and will get cool drafts in the house.
logging small time for years but just learning how, with a Forest stewardship plan, 2 compact Ford 4x4 tractors, 3point log arch, 8000# class excavator, lifts 2500# and sets logs on mill precisely where needed,  Peterson ATS upgraded to WPF mill, sugar maple/maple syrup a hobby gone amuck.

Offline Tim Crowley

  • member
  • *
  • Posts: 26
  • Age: 52
  • Location: Rochester, Vermont
  • Gender: Male
Re: Heat Exchanger Hook-up
« Reply #15 on: December 11, 2009, 10:13:06 am »
Thanks everyone.  These answers certainly help my conversations with my plumbers.  They're good guys, and they know what they're doing, but every system is different, so I like to at least ask them intelligent questions.  I think it makes me and them a little smarter about my particular system.  Of course, OWB's are not their specialty, so I like to make sure they're not making any wrong assumptions, etc.  It does seem to me that my goal should be to send 180 degree water to EACH system (baseboard and hot air), but the fact that they share the same boiler may make that impossible?

Thanks again.  I could NEVER have gotten this far with my OWB system without you guys. 

Tim

Offline Tim Crowley

  • member
  • *
  • Posts: 26
  • Age: 52
  • Location: Rochester, Vermont
  • Gender: Male
Re: Heat Exchanger Hook-up
« Reply #16 on: December 11, 2009, 10:17:06 am »
Hey Beenthere:  I just noticed your edit.  Thanks. When I looked at the diagram, I couldn't really tell, so thanks for taking another look!

Tim

Offline ken999

  • Full Member x2
  • ***
  • Posts: 110
Re: Heat Exchanger Hook-up
« Reply #17 on: December 15, 2009, 10:29:44 am »
Just a thought here...

Assuming your baseboard works best at 180, shouldn't you try sending water from the OWB to the exchanger at a HIGHER temp? You will loose some heat in the exchange, so it would seem logical to increase OWB temp until you get the correct temp on the 'house side'?

I'm not saying this is the overall solution to the problem, just something to think about/wondering out loud...

Offline SPIKER

  • Senior Member x2
  • *****
  • Posts: 1268
  • Location: Ohio Ashland County
  • Gender: Male
  • I'm new!
Re: Heat Exchanger Hook-up
« Reply #18 on: December 15, 2009, 06:20:02 pm »
Just a thought here...

Assuming your baseboard works best at 180, shouldn't you try sending water from the OWB to the exchanger at a HIGHER temp? You will loose some heat in the exchange, so it would seem logical to increase OWB temp until you get the correct temp on the 'house side'?

Ken: 180 is pretty warm, much more and a chance of a boil over or simply wasting wood is increased a LOT.   

Flow rate will only help some, the water has to stay in long enough to actually pass the heat to the rest of the system.   There is a calculation for heat exchangers that tells you how long the air has to stay in the exchanger to pick up the heat form the water.   while the higher the temp is the less time it needs to be in the exchanger.   You need to know Airflow, Water flow and inlet & outlet temps of both water & air.    (Cant remember if this was over a water to air exchanger or water to water?) prior to the room baseboards.?

In either way the baseboards will need the higher temp water as the water to air heat transfer is much less than what it is for the heat exchanger be it water to water or water to air as the heat exchanger has forced heat transfer dynamics.    The baseboard units if not powered are depending on convection heating to pull cool air in at bottom and warm air out the top...

Mark
I'm looking for help all the shrinks have given up on me :o

Offline ken999

  • Full Member x2
  • ***
  • Posts: 110
Re: Heat Exchanger Hook-up
« Reply #19 on: December 15, 2009, 08:31:31 pm »
Spiker- CB recommends running the e-Classics at 185 and the controller (at least mine) will not go above 195. If I wanted 180 on the house side of the plate exchanger, I'd try 185 at least.

Certainly getting the heat to the baseboard FIRST will help, if those zones are priority.

 